SS-V: 3010 Insulated Wall
Test No. VT02 Find temperatures at firebrick and insulating brick surfaces in an insulated wall.
Definition
A wall consists of two layers: a 9 inch firebrick layer and a 5 inch insulating brick layer. The temperature at firebrick surface is 3000 F and the temperature at the insulating brick surface is 80 F.
- Properties
 - Value
 - Firebrick Thermal Conductivity
 - 0.8 BTU/(hr-ft-F)
 - Firebrick Convection Coefficient
 - 12 BTU/(hr-ft2-F)
 - Insulating Brick Thermal Conductivity
 - 0.1 BTU/(hr-ft-F)
 - Insulating Brick Convection Coefficient
 - 2 BTU/(hr-ft2-F)
Results
              ![]() Figure 1. Boundary conditions  |
              ![]() Figure 2. Temperature distribution  |
| Reference* | SimSolid | % Difference | |
| Temp at Firebrick [deg-F] | 2957.0 | 2957.0 | 0.00% |
| Temp at Insulating Brick [deg-F] | 336.0 | 336.6 | 0.18% |
| Heat Flux Through Wall [BTU/9hr*ft2) | 513.0 | 525.6 | 2.46% |
*Reference solution is a 1D model.